    Cold shrinkable cable accessories series
    8.7/15kV Cold shrinkable cable accessories

    Scope of application:

    Apply to extruded insulated power cable with U08.7kV

    —Single-core, three-core cables
    Copper or aluminum conductor
    Extruded semi-conductive shield layer or semi-conductive tape shield
    Metal tape shield or metal wire shield
    Armoured or unarmoured
    Metal tape armoured or metal wire armoured


    Application:

    Indoor terminal: It is installed at the end of the cable running in the indoor environment (not exposed to wind, frost, rain, snow and sunlight), connected to power supply devices such as switchgear and transformer or busbar.

    Outdoor terminal: It is installed at the end of the cable running in the outdoor environment (can withstand wind, frost, rain, snow and sunlight), connected to power supply devices such as overhead cable, busbar, transformer and fuse or overhead cable.

    Straight-through joint: It is installed in the middle of a running cable, used to connect two sections of cable lines.




    Online inquiry
    Product details

    Technical Parameter:

    Conform to and pass GB/T12706.4-2020 rated voltage 1kV (Um=1.2kV) to 35kV (Um=40.5kV) extruded insulated power cable and accessories part four: rated voltage 6kV (Um=7.2kV) to 35kV (Um=40.5kV) power cable accessories testing requirements and IEC60502-4:2005 rated voltage 1kV (Um=1.2kV) to 35kV (Um=40.5kV) extruded insulated power cable and accessories part four: rated voltage 6kV (Um=7.2kV) to 30kV (Um=36kV) power cable accessories testing requirements.

    Serial Number ltem Standard Parameter Value
    1

    Power frequency withstand voltage test

    39kV, 5 min, no breakdown, no flashover

    2

    Direct-current withstand voltage test

    35kV, 15 min, no breakdown, no flashover

    3

    Partial discharge test

    Discharge is not greater than 10pC at 15kV

    4

    Impulse voltage test

    95kV, 10 times each for positive and negative polarity

    5

    Constant voltage load cycle (in the air)

    22kV, heated to 95-100, keep stable for 2 hours and circulate 30 times

    6

    Constant voltage load cycle (in water)

    22kV, heated to 95-100, keep stable for 2 hours and circulate 30 times

    7

    Short circuit thermal stability

    (cross-section of cable is 400 square millimeters

    40.9kA,3s,2 times
    8

    Short circuit dynamic stability

    (cross-section of cable is 400 square millimeters

    177.0kA,10ms,1 time
    9

    Power frequency withstand voltage test

    22kV, 15 min, no breakdown, no flashover

    10

    Outdoor terminal salt spray test

    11kV,1000h
    11

    Indoor terminal humidity test

    11kV,300h
    12

    Immersion test of intermediate joint

    2.5u0, heated to 95-100, keep stable for 2 hours and complete the immersion cycle for 30 times